Baseboard Heating Help

RoosterBoy
RoosterBoy Member Posts: 459
hi I need 44 feet of slantfin 30 installed and was wondering including baseboards the total run from the boiler will be 171 feet taco 007 is only good for 150 feet
what pump should my installer install

and will 171 feet including 44 feet of baseboard be ok or will I have a cold spot because of it being such a big loop
the room is only a 24x24 foot room

thanks

Comments

  • Geo_2
    Geo_2 Member Posts: 76
    007

    007 is a little to small, I would go w/ a 008
  • Tom_47
    Tom_47 Member Posts: 2
    Baseboard

    I have a Buderus G115 w a total of 90 feet of baseboard on the main floor. The total loop is roughly 195 feet. I added an additional 6 feet of High output Slant Fin to a room, which was sized by a plumbing house based on a heat loss analysis. The circulator is a 007 and has been doing the job for the past three years, however the new additon is not heating up to the rest of the house. Should I add more baseboard?, should I upgrade the circulator?, should I increase the reference temperature? please advise.
  • Tom_47
    Tom_47 Member Posts: 2
    Baseboard

    The previous message I forgot to tell you that the pipe is 3/4 inch. I have been told that I have exceeded the desired loop lenght, however is there a fix without dividing the loop?