Heating oil tank
John Boyer
Member Posts: 60
Today I tried to get my heating oil tank filled but when the guy started pumping in the oil it came back out the overflow. I know that the tank is not full can you think of a reason that this would happen?
0
Comments
-
too fast a fill?
vent clogged with spider webs and debris? take vent off see if it is clogged around the screen. send a tape measure down the fill and determine the depth of the oil...send a Wire fish down the fill see if some rather crafty ,chubby chipmonk tried to invade the home through the oil fill piping...i never said that chip monks were all that bright0 -
another thought
It could have also been that it was overfilled previous and the vent pipe never drained back into the tank...Either way you need to clean the vent and check the vent/whistle combo..:)0 -
Overfill
Is there one tank or two? Please describe the way the pipes feed to the tank(s), cross between the tank(s), and vent from the tank(s) Some pictures of the pipes and tanks would help.
Have you filled the tank(s) before without incident? How many times or how long (years months etc.)?
Regards
Ed Carey0 -
Overfill
Is there one tank or two? Please describe the way the pipes feed to the tank(s), cross between the tank(s), and vent from the tank(s) Some pictures of the pipes and tanks would help.
Have you filled the tank(s) before without incident? How many times or how long (years months etc.)? Is this a new oil delivery company?
Regards
Ed Carey0 -
Overfill
Is there one tank or two? Please describe the way the pipes feed to the tank(s), cross between the tank(s),
and vent from the tank(s) Some pictures of the pipes and tanks would help.
Have you filled the tank(s) before without incident? How many times or how long (years months etc.)? Is this a new oil delivery company?
Your answers to these questions will help us provide answers to your questions.
Regards
Ed Carey0 -
Thanks
That is what had happened the company I had been using over filled the tank every single time they came. So after several phone calls with the new company we figured out that the vent pipe had old fuel in it so it was vaporlocked. We blew it out with an air compressor and that seemed to do the trick.0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements