oil burner reset

al leone
al leone Member Posts: 25
I have and oil burning steam boiler.
I tuned on the t-stat today , no heat I checked the sys,and pressed the reset button on the Carlin burner, It ran for a minute, with a flame and them shut down on the reset again.
I have 1/2 full oil tank, and am gettin plenty of oil.
Im a plumber, not an oil burner tech. any Ideas.

Comments

  • Mijola
    Mijola Member Posts: 124
    the points

    Sounds like the points need to be adjusted. Every few years the points wear off and you have to reset them with your feeler guage.
  • Mijola
    Mijola Member Posts: 124
    the points

    Sounds like the points need to be adjusted. Every few years the points wear off and you have to reset them with your feeler guage.
  • Mijola
    Mijola Member Posts: 124
    the points

    Sounds like the points need to be adjusted. Every few years the points wear off and you have to reset them with your feeler guage.
  • Mijola
    Mijola Member Posts: 124
    the points

    Sounds like the points need to be adjusted. Every few years the points wear off and you have to reset them with your feeler guage.
  • Mijola
    Mijola Member Posts: 124
    the points

    Sounds like the points need to be adjusted. Every few years the points wear off and you have to reset them with your feeler guage.
  • Mijola
    Mijola Member Posts: 124
    the points

    Sounds like the points need to be adjusted. Every few years the points wear off and you have to reset them with your feeler guage.
  • tommyoil
    tommyoil Member Posts: 612
    Questions

    Does it run with flame right up until the moment of lockout? OR does it lose flame along the way (as if the oil is being restricted) and then die out. If it quits with full flame at lockout it sounds like a dirty /defective cad cell eye or associated wiring. Or possibly the control itself.
  • David Sutton_5
    David Sutton_5 Member Posts: 87
    Hello Al

    Al if you hit the reset and it ran up to the safty time 45 sec. with a astablished flame, try this take a set of jumpers or a sckrew driver hit the reset and jump out the
    F+F terrminels and see if it keeps running past the safty time if not its probly the control if it keeps going and dose not shut down its the lead or the cad cell ...David
  • Steve Eayrs
    Steve Eayrs Member Posts: 424
    Could be a number of things.

    Points (electrodes) are only one possiblility.
    COUld be plugged nozzle, bad burner transformer, dirty cad cell, bad primary control, or other.

    Unless you have a a lot of time and money, to just start replacng all the moving parts, it would be cheaper to get someone to fix it who can determine which part is needed. Usually will only take min. service call to troubleshoot and fix.....unless you have a lot of other problems too.

    Steve
  • lchmb
    lchmb Member Posts: 2,997
    just curious

    When was the last time it was serviced??
  • Maine doug_2
    Maine doug_2 Member Posts: 16
    Please Note

    The above 6 copies are not from me, the Maine doug.
    Guess I will have to do like Maine Ken

    Maine doug
  • Firedragon_4
    Firedragon_4 Member Posts: 1,436
    All of the free advice is nice,

    but you're playing with fire and your property and maybe your family's lives, call a pro!
  • ed wallace
    ed wallace Member Posts: 1,613
    oil burner reset

    please call for help easier then dialing 911