Check out this near boiler piping
Brian in Indy
Member Posts: 15
First, many thanks to the forum, tonight I received "We've got steam heat", which I've devoured, now into Lost Art. We're restoring an older home with a newer WM LGB boiler. The system was designed by Hoffman back in the day, there is a main vent (new) at the end of the return and a new F&T connecting the supply and return at the end of the main. There is condensate receiver and pump. Some thoughts:
(1) the vent on the receiver should be higher, right?
(2) I am somewhat confused by the equalizer - is this supposed to be at the end of the main or in the boiler room? As you can see from the pics, I have two 4" risers going into the 4"header, there is no drip leg (right?).
Please comment, I've had some knuckleheads out and am searching for a competent person, and want to be informed.
THANKS
Brian
(1) the vent on the receiver should be higher, right?
(2) I am somewhat confused by the equalizer - is this supposed to be at the end of the main or in the boiler room? As you can see from the pics, I have two 4" risers going into the 4"header, there is no drip leg (right?).
Please comment, I've had some knuckleheads out and am searching for a competent person, and want to be informed.
THANKS
Brian
0
Comments
-
my thoughts are (is)
enlighten me as to why on earth does a house need a boiler feed or condensate tank/pump....whenever i see a feed pump i want to know if the original system had one...if not someone's treating a symptom but not the problem...gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Equalizer?
I didn't see one.
The supplies on the LGB come off the rear portion of the end sections and the return taps are in the front.
I see what look like two risers coming of the rear of the boiler and NO equalizer.
Is that a "boiler feed tank" controlled by the LWCO, or is it a "condensate pump" that is controlled by a float in the receiver?
Has anyone sized the connected load of EDR in the house?
While I have been in homes where an LGB-4 or 5 are necessary, they have been few.
I also have concerns about the rusting I see on the top of the boiler toward the rear of the boiler where the collector hood and draft hood meet.
And just so this post finishes on a positive note, the insulator did a nice job.
Mark H
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements