Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
heating calc.
Matt_21
Member Posts: 140
i just completed a heating load calc for a customer with some new software. the weather info was based on the ashrae calcs in the program. should i size the boiler based on the heat load or add 10-20% as a safety factor. i think the ashrae data is based on the average weather 97.5% of the time in the heating season in an average winter. i'm concerned about those times we have cold snap for a week or so.
0
Comments
-
design conditions
if u stick to design loads. your system will carry you thru those cold snaps.
but use design loads. not the average weather for 97.5% of the year...
my .02 worth.
EIN
0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements