vents on a 2 pipe base board steam system
John Lasky
Member Posts: 35
good afternoon,
thank you for this site its been a great help for various problems Ive had to deal with in my home and others.
I have a steam heat system in a 2 floor house in upstate NY , the house is 75 year old.
The first floor has cast iron base-boards (burnham base Ray) and is a 2 pipe system ,the second floor is one pipe radiators .
My question concerns the first floor.
Again the first floor is a 2 pipe base board system that does not have "traps".
The return piping does drop to floor level in the basement and enters the boiler at floor level. (the boiler is a 4year old HB Smith ) , should there be air vents on the base boards??
There were vents on every baseboard unit when I bought the house and I have since installed new vents in all 5 rooms. they get very hot (lots of hammer).
the longest baseboard is 16' the shortest is 3 foot. Im not sure if the system is running right or getting too hot.
many thanks "John"
thank you for this site its been a great help for various problems Ive had to deal with in my home and others.
I have a steam heat system in a 2 floor house in upstate NY , the house is 75 year old.
The first floor has cast iron base-boards (burnham base Ray) and is a 2 pipe system ,the second floor is one pipe radiators .
My question concerns the first floor.
Again the first floor is a 2 pipe base board system that does not have "traps".
The return piping does drop to floor level in the basement and enters the boiler at floor level. (the boiler is a 4year old HB Smith ) , should there be air vents on the base boards??
There were vents on every baseboard unit when I bought the house and I have since installed new vents in all 5 rooms. they get very hot (lots of hammer).
the longest baseboard is 16' the shortest is 3 foot. Im not sure if the system is running right or getting too hot.
many thanks "John"
0
Comments
-
This is set up as 2-pipe air-vent
The return line from each Baseray must drop to basement floor level, or at least below the boiler's waterline, before connecting with any other return line. Otherwise steam will enter the returns and cause banging.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements