Main vent sizing?
Matt_28
Member Posts: 34
Hello, I think my main vent pipe sizes are small and would appreciate any help in finding replacements. Currently, my radiator vents are noisy and I am realizing that they are doing most of the work to vent my system. I have 2 mains with Vent-Rite #35's just before the drop to the water line. My main lengths are as follows:
1. 25'x2 with a 9', 8', 8', 15' & 15' branch to radiators (I am unsure of the branch sizes) and a 8'x1.25 return.
2. 35'x2 with a 6', 17', 5', & 13' branch to radiators (I am unsure of the branch sizes) with a 3'x1.25 return
Thanks for any responses and all the help I have had from The Wall in the past.
Matt
1. 25'x2 with a 9', 8', 8', 15' & 15' branch to radiators (I am unsure of the branch sizes) and a 8'x1.25 return.
2. 35'x2 with a 6', 17', 5', & 13' branch to radiators (I am unsure of the branch sizes) with a 3'x1.25 return
Thanks for any responses and all the help I have had from The Wall in the past.
Matt
0
Comments
-
That's Easy
Two Gorton #1 or Hoffman #75 vents on the long main, one on the short main. I see this combination all the time and the above sizes work great.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
alternatives?
Is there any one vent that is equal to two Hoffman 75s or Gordon 1s? I am hoping that I will not have to branch off the existing riser to add two vents to the long main.
Thanks for you help Steamhead.
Matt0 -
main vent sizing
When adding a second main vent what is the correct way to pipe this?0 -
All you need to do
is screw a tee onto the existing vent riser with the run vertical, and screw one vent into the top of the run. Screw a 90-degree street ell into the bull of the tee, with the female end pointing up, and screw the second vent into that.
Simple!
No, I don't know of an intermediate-capacity vent like you mention. This is why we commonly use two vents on some mains.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements