relief valve popping

jeff dustin
Member Posts: 3
I got a call that my customer's relief valve was popping. I show up and find the expansion tank water logged. I changed the pop safety valve and expansion tank. Well I just got a call back from the customer and the pop safety is blowing again! The boiler is a slant fin hot water boiler 109,000 btu with 6 zones including a domestic hot water, 30 lb. pop saftey, #30 extrol tank, and the system also has anti-freeze in it. Need help! Any Answers?
0
Comments
-
What pressure is the water feed feeding the boiler to? With 6 zones a # 30 might be too small. You might have to use a #60 Does this boiler have a domestic hot water coil? If so it might be slowly leaking domestic water pressure into the boiler0 -
Relief Valve
I agree with F.F. the Tank may be too small or the domestic coil could be leaking. Or- the auto or hand feed valve may be bypassing. If the tank wasn't new I would also suggest the tank diaphragm could be ruptured.0 -
Piping
Isolate domestic water to eliminate that as a problem.
Also look at system piping, make sure feed vlave isn't being pulled open when the circulator is running.0 -
relief valve popping
The autmatic feed is shut-off due to the anti-freeze in system. the domestic hot water is a boiler mate.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 943 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements