Installing a hydro air coil with an outdoor re-set.

Any limits to high and low water temps.

Using a Munchkin with Vision I.

Usually don't deal with Hydo air.

Comments

  • Ted_9
    Ted_9 Member Posts: 1,718


    Remember, you dont want low temp water for hydro-air. It will feel cool, not warm. So other than controling you domestic water, why are you using the vision 1?

    PATRIOT HEATING & COOLING, INC.
  • R. Swatton
    R. Swatton Member Posts: 86
    vision I

  • R. Swatton
    R. Swatton Member Posts: 86
    Vision I

    I also have some baseboard zones.
  • Ted_9
    Ted_9 Member Posts: 1,718


    Go with vision one and vision two then. You can control different temp water. Like a higher temp for the hydro-air and then over size your baseboard and use a lower temp water.

    Just a thought.

    PATRIOT HEATING & COOLING, INC.
  • Keep your hydro-air

    temps between 140 to 150 for a good air exchange and no complaintsof cold air. It is also important to get the air flow balance in CFM so you never have the blower running with a temp in the supply less than 100 degrees.
  • Ted is right

    and if you balance it correctly the boiler temp never has to go above 150 degrees.