Vaporstat & Pressure Gauge Selection

Firedragon_4
Firedragon_4 Member Posts: 1,436
L408A and a 48 oz gauge, JMO.

Set the MAIN at 16 oz. and the DIFF at 12, way to go!

Comments

  • Fibercop75
    Fibercop75 Member Posts: 2
    Vaporstat and Pressure Gauge Selection

    Boiler is Crown JBF52 150 Kbtu gas steam, all rads hot before any deflection on stock 30 PSI gauge. Existing PA404A ptrol won't cut out at <5 PSI at min. setting so it's got to go. Should I use a 16 oz/in or 4 PSI max pressure vaporstat and a 20 Oz/in or 5 PSI gauge? I was leaning toward the 16 oz vstat and 20 oz gauge. Also, recommendations for intital settings? Thanks!