Vaporstat & Pressure Gauge Selection
Firedragon_4
Member Posts: 1,436
L408A and a 48 oz gauge, JMO.
Set the MAIN at 16 oz. and the DIFF at 12, way to go!
Set the MAIN at 16 oz. and the DIFF at 12, way to go!
0
Comments
-
Vaporstat and Pressure Gauge Selection
Boiler is Crown JBF52 150 Kbtu gas steam, all rads hot before any deflection on stock 30 PSI gauge. Existing PA404A ptrol won't cut out at <5 PSI at min. setting so it's got to go. Should I use a 16 oz/in or 4 PSI max pressure vaporstat and a 20 Oz/in or 5 PSI gauge? I was leaning toward the 16 oz vstat and 20 oz gauge. Also, recommendations for intital settings? Thanks!0 -
George,
why aren't you at Chowdafest?0 -
A few personal problems
kept me away. I also missed the CO panel at ISH, but family comes first!0 -
Geaorge
> kept me away. I also missed the CO panel at ISH,
> but family comes first!
0 -
George
Hope its not too serious. Wish you well !!0 -
Thanks tommyoil,
it's very serious and is in regards to my wife, major clinical depression. Thanks for asking, FACT!0 -
0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 65 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements