improving an existing hot water base board system

Donald Raines
Member Posts: 1
A new home (7 years) with a hot water baseboard system. Not adequate for winter cold. Limited wall space because almost 25% of wall space is window walls where baseboard tubes cannot be run. Any suggestions?
0
Comments
-
Panel Radiators
Less wall space and nice even heat0 -
Many options
Like Dave said, they make panel rads that can be as high as a wall and only 2 ft wide. Fan coils are available both as surface and wall insert (or in-floor) mount. If you have AC cooling ducts, you might also think about putting a hydro-coil in the air handler and run some forced warm air into the room. Radiant flooring could be done staple-up from the basement or a quick track tubing system could be layed over the current sub-floor. I sure others can come up with even more ideas.0 -
Higher capacity baseboard
Most homes use standard residential baseboard about 7 1/2 inches tall and 2 1/4 inches deep. If you go to high output baseboard...about 8 3/4 inches tall and 3 inches deep.....you can get about 60% more output in the same length.
Boilerpro0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 943 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements