Anticipator Setting

Randy_7
Randy_7 Member Posts: 23
Just installed new Taco zone valve but am not sure if I should set the thermostat anticipator at the boiler gas valve current (0.5 amps) or Taco valve current (0.9 amps)? Taco recommends the 0.9 amp setting. Recommendations would certainly be appreciated.

Randy

Comments

  • Boston Boiler
    Boston Boiler Member Posts: 70
    Randy

    0.9 is your setting.

    BB
  • Firedragon_4
    Firedragon_4 Member Posts: 1,436
    Be careful,

    if it's a 555 it needs to be at 0.9 which is the left side of the scale on a T87, but if it's a new ESP it should be at 0.09 which is the right side of the scale. BTW, the only correct way to do this is with an meter, FACT!
  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    And .9 is only a starting point

    Most hydronic systems work better with longer run times. If I remeber right this will give you a cycle time of 6 times per hour. Most systems work better at 3 to 2 per hour. I typically set the anticipator as high as possible and then turn it back as needed to achieve smooth temp control.

    Boilerpro
  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    And .9 is only a starting point

    Most hydronic systems work better with longer run times. If I remeber right this will give you a cycle time of 6 times per hour. Most systems work better at 3 to 2 per hour. I typically set the anticipator as high as possible and then turn it back as needed to achieve smooth temp control.

    Boilerpro
  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    And .9 is only a starting point

    Most hydronic systems work better with longer run times. If I remeber right this will give you a cycle time of 6 times per hour. Most systems work better at 3 to 2 per hour. I typically set the anticipator as high as possible and then turn it back as needed to achieve smooth temp control.

    Boilerpro