Lennox Furnace Model number 80mgf2-60a-2
Roy Tenn
Roy Tenn Member Posts: 15
Hi All,
I was on a service call on this unit where the furnace cycles on and off on the pressure switch. I jumpered the PS
as soon as the furnace started and it ran normal until tstat satified. I recall Lennox had a kit (new PS and ventor, where the sensing tube is at the bottom of ventor)replacement for the G24 series. Is this furnace similar to the G24 and if so is the replacement the fix?
Thanks in advance, Roy
  • Brian_24
    Brian_24 Member Posts: 76
    What is the pressure at the switch when the furnace is running pre-purge and when it is firing? Maybe the inducer isn't up to speed.
  • Ken D.
    Ken D. Member Posts: 836
    Lennox
    Check to be sure theere are no blockages in the flue, vent or exhaust area. Check for moisture in the press. switch or tubing. If a condensing furnace, check for condensate area restrictions.
  • Glenn Harrison_2
    Glenn Harrison_2 Member Posts: 845
    G24 and 80MGF use the same kits
    you just have to get the appropriate kit for your size furnace.
    Just to be sure, the 80 MGF your working on, does it have a black painted housing on the inducer? If so, then you need the Pressure switch kit, which does include the pressure switch, Inducer motor, and gaskets.
  • Roy Tenn
    Lennox
    Thank you all for the reply. I will check into all your suggestions.
    Roy
  • Roy Tenn
    Lennox
    Roy
