Expansiion Tank Test
Paul_28
Paul_28 Member Posts: 113
Can I test the air pressure in the tank on the bioler?
  • Alan_6
    Alan_6 Member Posts: 87
    expansion tanks
    Are you talking about a bladder tank?
  • Paul_28
    Yes
  • Alan_6
    tire guage
    You can test them with a tire pressure guage. The pressure should match your system pressure. Some people think they can tell if they are water logged, by tapping on the tank, and hearing a hollow sound. This does not work, when a tank is water logged, the pressure will increase rapidly, as the water warms up. Usually if you find the pressure very low it is too late, the bladder has already over stretched.
  • larry_9
    larry_9 Member Posts: 33
    Test Bladder tank
    One quick way of testing a badder Tank is to shut the valve going into the boiler and watch the pressure guage if it dropes and then when you open it and it raises you badder tank is eiather under sized or water logged.
  • Al Letellier
    Al Letellier Member Posts: 781
    Xtank pressure check
    you must chech the pressure in the tank WITH NO PRESSURE on the system side of the tank. That means that if there is no isolation valve, you must lower the system pressure to 0 and then check and adjust the tank pressure to the normal operating pressure of the system, then watch it for 10-15 minutes to make sure it is stable. If it drops, replace the tank. Then you must refill the system to normal pressure and make sure you get all the air out. If you're not familiar with these proper proceedures, hire a pro......an often used phrase, but well worth doing!!!!
  • Boston Boiler
    Boston Boiler Member Posts: 70
    Tip
    You must be asking because you think there may be a problem
    and if in fact there is and you are determined to change the tank yourself rather than calling a pro here is a tip.
    A water logged tank is heavy and when you are unscrewing it and the last thread comes off be prepared for a forcefull and unexpected downward drop, don't let that last thread catch you off guard. Also when the new one goes in tighten it with a wrench, NOT by hold the tank and turning it. Holding the tank and turning it works nicely but you can easily break the weld.
    BB
  • hr
    hr Member Posts: 6,106
    And if you are going to
    change it out, or remove it, make sure the boiler is not up to 180° :) Hot and heavy is a really bad mix!
    hot rod
  • Firedragon_4
    Firedragon_4 Member Posts: 1,434
    Great point rod, and
    why I pull the Schrader valve guts out, punch a hole in the top and drain them first.
    Once had an apprentice who broke his foot when a #60 landed on it after slipping through his hands!
  • John M_2
    John M_2 Member Posts: 1
    expansion tank size
    How do I know the correct capacity expansion tank to get when switching from an old (and leaking) pressure tank to a diaphram expansion tank?
  • Firedragon_4
    Here ya go:
    http://www.amtrol.com/website/content.nsf
    But you may want to have a pro do this.
  • DaveC
    DaveC Member Posts: 201
    Sneaky tanks!
    On the same job, I had 2 bad experiences with the tank replacement. First, the waterlogged tank slipped out of my hands and landed perfectly into the slightly larger diameter bucket I had placed below it - sending a column of hot, foul-smelling water right up into my face (as I admired it's descent). Then, the replacement tank split the air scoop, just as I made the final tightening turn (the threads felt loose, so I put several wraps of teflon tape on them - could that have caused the split?).
    They feel so "beachball" light when empty, though! :^0
  • SRTECH
    SRTECH Member Posts: 5
    EXPANSION TANK TEST
    ONE WAY TO DETERMINE IF YOUR EXPANSION TANK IS BAD,IS TO HEAT YOUR BOILER UP 10 DEGREES.MAKE NOTE OF THE PRESSURE IN THE SYSTEM AND THE TEMPERATURE. THERE SHOULD ONLY BE A MAXIMUM OF 2LBS(PSI) RISE FOR A 10 DEGREE INCREASE IN TEMP.IF IT EXCEEDS THIS PRESSURE RISE IT IS EITHER BAD OR UNDERSIZED.IF YOU DO REPLACE IT A GOOD IDEA WOULD BE TO PUT A 1/2" THREADED BALL VALVE AND A 1/2"X2" BLACK NIPPLE ABOVE IT FOR FUTURE PROBLEMS.