air vent
Campo
Member Posts: 17
I am working on an original hoffman controled heat system. All thermostatic trap elements have been replaced including the ones at the end of the mains. We, however, are still having trouble getting heat to the ends, which is especially a problem because the thermostat is in a back appartment. The other appartments overheat. Should I add vents to the ends of the mains? Or, there might be a problem with the main vent by the differential loop (single pipe type loop). How would I replace or redo this main vent as it is a Hoffman No. 15, and I'm sure they don't make these anymore.
Thanks for all your help. This forum is great!
Campo
Thanks for all your help. This forum is great!
Campo
0
Comments
-
another thought
Could I eliminate the traps that go between the ends of the steam mains and the dry returns. Then cap where it enterd the dry return and add a large vent or two to the end of the main?
Just another idea.0 -
Take the vent out to test...
If you remove temporarily the vent, you can eliminate any air problems from your troubleshooting.
If you get steam at the vent location, find the leaking trap.
If it still doesn't heat every riser to every radiator, and the radiator is on with an open trap, you are running out of steam.
That usually is caused by missing insulation, which increases the load on that pipe so much, that it no longer is large enough to supply steam to what's connected to it.
Is the boiler big enough and fired at rating? Is it clean and well adjusted?
Noel0 -
That's a possibility
but try Noel's recommendation first. If the #15 vent is bad, replace it with a Gorton #2.
www.gorton-valves.com
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements