Pipe Sizing
EJW
Member Posts: 321
Can anyone tell me the maximum btu load of 3/4 copper?
0
Comments
-
If
your working with a 20 degree delta T about 55 mbh.
Regards
Robert
Me0 -
Sizing
Yes it is a Delta of 20. Thank you sir, EJW0 -
EJW,
This may be of help to you for the future.
By the way, 3/4" is good for 40,000 btu's, 4 gpm @ 20° ∆T0 -
Figure i
gave was for 5.5 gpm and the question was about maximum capacity.
I'd be more comfortable designing for 4gpm at 40 mbh.
My data was from Weil Mclean and the chart has never failed me!
Regards
Robert0 -
That's interesting, Robert,
Your Weil Mclain sheet says 5.5 max, and the B&G says max 4.0, and I believe Dan's books show 4.0/40,000 btu's also. I'm curious how W.M. came up with 5.5.0 -
I also wrote
Zoning Made Easy for B&G. My numbers are based on B&G's System Syzer, developed by my old teacher, Gil Carlson.Retired and loving it.0 -
Wow,
that means I've been carrying a Dan Holohan book around with me for over 10 years and didn't even know it.
Thanks, Dan. I had no idea you wrote that.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements