oil piping

Matt_21
Matt_21 Member Posts: 140
i have two new 330 gallons oil tanks we are installing in a school. i was planning on coming out of the tanks and tie into one 1/2" steel pipe, run to the two smith 1,000,000 btu boilers (each is 1 mill btu) tee the 1/2" pipe and reduce to the pipe size on the burner. will 1/2" be large enough or is there a book or something i can buy which helps with sizing? the run is about 20' and will run along the floor.

Comments

  • dconnors
    dconnors Member Posts: 215
    Yes

    According to my Suntec Pump book you should be fine.

    L=6+.75h/.00218H
    L=line
    H= lift
    Q= firing rate in gph
  • Matt_21
    Matt_21 Member Posts: 140
    thanks dave

  • Jeff Krawic
    Jeff Krawic Member Posts: 58
    oil piping

    Need to be careful here.......... 2 pipe system or 1 pipe? TGS (total gearset) ((Gearset capacity)) of each pump if 2 pipe will pass through suction line. Should be gravity feed if tanks are same height as burners and you will get away with 1 pipe. Webster and Suntec and Tuthill and Hayes all have charts to go by. As long as you have the right info to put in first. Good Luck.