oil piping
Matt_21
Member Posts: 140
i have two new 330 gallons oil tanks we are installing in a school. i was planning on coming out of the tanks and tie into one 1/2" steel pipe, run to the two smith 1,000,000 btu boilers (each is 1 mill btu) tee the 1/2" pipe and reduce to the pipe size on the burner. will 1/2" be large enough or is there a book or something i can buy which helps with sizing? the run is about 20' and will run along the floor.
0
Comments
-
Yes
According to my Suntec Pump book you should be fine.
L=6+.75h/.00218H
L=line
H= lift
Q= firing rate in gph0 -
thanks dave
0 -
oil piping
Need to be careful here.......... 2 pipe system or 1 pipe? TGS (total gearset) ((Gearset capacity)) of each pump if 2 pipe will pass through suction line. Should be gravity feed if tanks are same height as burners and you will get away with 1 pipe. Webster and Suntec and Tuthill and Hayes all have charts to go by. As long as you have the right info to put in first. Good Luck.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements