insulating undergroungd steam returns?
tim smith
tim smith Member Posts: 2,886
What do you guys suggest, we are presently repiping all the old underground condensate pipes on a house, old piping had no insulation or protection, just buried in dirt, very dry hill side home. Wondering what thoughts you all have on insulation/protection for piping on this. Any comments welcomed. Thanks in advance Tim.
    Steamhead Member Posts: 18,217
    Don't run them underground if you can avoid it
    but if you have to, copper will last longer than black pipe.
    Do not use copper on any pipe that carries steam.
    Consulting
  • tim smith
    Steam head
    Steamhead, what about insulating, what do you think. has to go underground due to radiator elevation to boiler ht.
    You want to keep them dry
    maybe insulate them and encase them in gravel before backfilling. If there is a drain or sump-pump in the area you might want to route any water there from the gravel bed.
    Consulting
  • Brad White_2
    Brad White_2 Member Posts: 188
    Careful of gravel
    with expansion and contraction gravel (crushed stone) will shred any insulation if not the pipe itself. I would suggest insulating in fiberglass, at least an inch thick, then sliding a piece of SCH 40 PVC pipe over the buried portion. Seal the ends with spray foam and paint for UV protection. Just a thought.
  • tim smith
    Thanks guy's for the input
  • We insulate
    all under floor/ground piping w/ foam insulation. Available @ any insulation supply house. Did our first steam return w/ foam 25+ years ago. Still there.
  • clammy
    clammy Member Posts: 3,242
    trouth
    I don't think it's speeld right but i've done this a number of times with great success .You install a drainage trouth and run your returns in it and just get 4 ft section of steel to cover it ,it good for basemnts and buried returns it leave you acess to it for good and is well worth it later for service should promblem arise .I personally would insulate it with fiberglass and do it in steel it lasted 40 or 50 years and i've seen them last 90 just use tee's instead of 90 where it makes sense for flushing good luck and peace clammy
    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
  • Tom Blackwell
    Tom Blackwell Member Posts: 20
    It depends on where the heat from the uninsulated pipe goes. If the heat loss ends up un the basement or house, then there is no need to add insulation because the btu's aren't wasted. If, however the losses don't end up in the house, then insulation would be needed. Fiberglass with a pvc outer jacket works well in a dry environment.
  • tim smith
    Thanks guy's
    We finished and backfilled yesterday, replaced all undergrounds with steel (domestic)! Insulated with fiberglass also. There is no ground water on the hill here so was not worried about water. The old pipe had no insulation and had 0 sign of exterior corrosion except in the area where it corrode from inside out. Then proceeded in corroded outside of pipe. Old return was 70 yrs old, not bad. Concrete gets poured tommorow.