circulator orientation
aktom
Member Posts: 4
what is the best way to orient a circulator on a horizontal pipe run? I believe I read where shafts sould always be horizontal.
thanks for any replies
thanks for any replies
0
Comments
-
true story....
although...you can go vertical if and only if the system pressure is ABOVE 20 psi....kpc0 -
Yep!
Motors horizontal and electrical box/connections on top.If this seems to be a problem, almost all waterlubed circulators on the market can be disconnected from the pump housing(4 screws/allenheads) and turned 180°. This will get the electrical connection on top.Keep in mind...they will ONLY turn 180°, not 90°!
P.S. For all to see.....If you ever change a motor on a Grundfos 15-42/58 and have to junk it, SAVE THE SCREWS.
I was in a bind a few months back. The screw on my Sawzall rounded out.(what are the chances?He He He.)Lo and behold, the screw from a Grundfos motor fit exactly! They are also made of a much higher grade metal than the 50 cent replacement from the hardware store. Us Yankees find things in a mysterious way but it works! (see, you all thought you wouldn't learn something today, but dammit, you did!) Chris0 -
Why not 90° Chris?
The Grundfos Super Brute 15-58s I use will allow a 90° motor position. as long as the cover to the electricail clears.
Good score on the allen heads for the sawzall! I'm pretty sure the Grundfos screws are metric. I know metric allen wrenches fit better than US sizes.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Why not 90° Chris?
I've turned 15-58 Super Bruted 1/4 turn.
Good tip on the allen screws. I'm pretty sure the Grundfos screws are metric. The metric allen wrenches fit better the US sizes.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
The instruction sheet for the BruteII calls for the terminal box on one side or the other w/ the conduit entry facing down. The allen screws are 4mm. From the sheet "the pump must be installed w/ the motor shaft positioned horizontally. Under no circumstances should the pump be installed with the shaft vertical or where the shaftfalls below the horizontal plane."
For what its worth!!!
Ken0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements