No Heat Upstairs
Michael_14
Member Posts: 1
I have a Reznor gas boiler and there is no heat upstairs. The little guide I got from the house inspection says to add water if the PSI is less than 10-12. Well I have 15 PSI so I don't know if that's a good idea. I have bled all the radiators upstairs - nothing. I can feel the pipes coming out from the boiler for upstairs are cold, but the valves on each seem to be open. The temperature on the boiler seems low though now at 90 degrees, when last night it was 150 degrees. PLease help! Thank you so much!!! Michael
Michael
I do not have enough info. Do you have heat downstairs? (you said no heat upstairs). If you have heat downstairs then upstairs is on its own pipe. Do you have a thermostat upstairs? If you do, it must have a valve or pump on the 2nd floor pipe.........this could be the problem......The system at 12 to 15psi should be OK and if you get water out of the vents on the 2nd floor that part should be OK. Can you send a picture or drawing of the pipes off the boiler? This might help.0 -
No Heat
Possible circulator not running, zone valve or solenoid not opening, flow valve stuck, system airbound,etc. If it is baseboard convectors, is the airspace beneath the convector unrestricted? Is the boiler firing OK? Downstairs is fine I take it.Is the thermostat set properly and is it calibrated OK? Try turning stat all the way up temporarily to see if that helps. Could be in control system as well as water system.0 -
Air Lock?
How high is upstairs? If you have three floors, 15psi may not quite do it. If you have six floors, it won't do it.
If you have a converted gravity system (big pipes), maybe you don't have a big enough circulator.0
- 86.9K THE MAIN WALL
- 57 Biomass
- 109 Chimneys & Flues
- 5.7K Gas Heating
- 105 Geothermal
- 70 Pipe Deterioration
- 971 Plumbing
- 6.3K Radiant Heating
- 386 Solar
- 15.4K Strictly Steam
- 44 Industry Classes
