wiring question
ed wallace
Member Posts: 1,612
i am wiring a boiler with a taco 504 control and 5 circulaters how many 14 gauge wires can i run inside 1/2 inch emt
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=256&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
The NEC says:
If you run THHN (typical) you can run 12, 14-GA conductors in 1/2" EMT.
If you run RH, you can only run 6.
wiring
i didnt think you could run that many wires in 1/2 conduit
Ed, you might want to confirm that number under MA code.
BB0 -
What about using
all the same gauge wires , but having some of them low voltage and some line voltage in the same conduit ? Is this forbidden ?0 -
sometimes
they are, if the wire is rated the same, with low voltage wiring that is harder to find, mard0 -
If I'm correct you can have 9 current carying wires in a pipe before you have to derate circuits (ampacity) since small circ. pumps draw very little I'd guess you'd be all right with all 5 pumps in pipe.....you didn't give enough info on what your going with the wiring in the pipe.....so it's only a guess0 -
wiring
I am in Ma. its 5 taco 007s contolled by a taco504 controller
- 87.4K THE MAIN WALL