W/M GV boilers, cleaning heatx gas side

tim smith
tim smith Member Posts: 2,807
Just wondering how you guys go about it. We are finding that in 7 - 10 yr old weil mclaing GV boilers, they are getting a fair amount of build up in heat x. Can only get to a portion of heat x through burner port and through flue breach. Get poor combustion if you don't take boiler apart and separate sections and brush and wash out, then reassemble w/ new gaskets and then she purrs along again. Tough job, all day. Any other solutions you guys have found?

Comments

  • jerry_6
    jerry_6 Member Posts: 4
    wm GV boilers

    that boiler will only foul up if a bypass line is not installed.review the install guide before running it again.
  • Mike Reavis_2
    Mike Reavis_2 Member Posts: 307
    The GV is not a condensing boiler as you know.

    but the boiler is commonly field piped "in and out" on converted gravity systems, and systems with large water volume. As was previously mentioned, follow the piping diagrams. Weil has required pri-sec piping for more than 10 years on the GV.