Radiant setup

neuro
neuro Member Posts: 7
Radiant floor heating: 3 zones, all to run at 101 degree F, total flow 6.1 gpm /7.4 head. I am using an electric boiler as my heat source.
My questions:Am I better to control with 1 circulator and 3 zone valves or each zone have its own circulator.
I am also looking at boilers Slant/Fin Monitron & Weil McLain P-ER. All opions greatly appreciated. Thanks

Comments

  • well if ....

    it was my job I would use circulators...Grundfos 15-58...has 3 spd. control built in so you can customize ....kpc
  • Chris_32
    Chris_32 Member Posts: 19
    Valves

    I would recommend valves as splitting 6.1 gpm three ways with pumps is not a cost effective solution. It requires more controls and consumes more electricity over the long run not to mention that almost anybodies small wet rotor circ can handle 6 gpm at 7 or 8 ft.

    I would most likely use 1 pump and zone at the radiant manifold with loop valve actuators.
  • Nron_9
    Nron_9 Member Posts: 237


    I agree with chris though with a system this small do you need 3 zones are they heating different areas if they all require the same temp try useing balancing valves to even out your system .
  • eleft_4
    eleft_4 Member Posts: 509


    Neuro, Chris, Nron, et.al,
    Don't forget one of these.

    al
  • eleft_4
    eleft_4 Member Posts: 509
    include this

  • neuro
    neuro Member Posts: 7
    radiant setup

    Nron, I am heating basement 6 loops w/1/2" pipe,in slab 1stfloor 8 loops w/3/8" & 2nd floor 9 loops w/3/8" Rhau pannls. Total about 61,000 BTU's
  • neuro
    neuro Member Posts: 7
    PSI regulator

    eleft Who makes the differentat pressurs regulator
  • eleft_4
    eleft_4 Member Posts: 509
    D. P. regulator

    Sorry,
    This is a Honeywell model D 146, Danfoss also has them.

    al
  • Joe_51
    Joe_51 Member Posts: 101


    I;m only a HO but those numbers you cited seem awfully low compared to the data you just supplied above.....