underfireing buderus
RoosterBoy
Member Posts: 459
has anyone had a problem underfireing a buderus g115 boiler
by 5 to 10% I will be using a power Venter so I should not have the problem of expelling the gasses of combustion
right? will condensing be an issue?
thanks
John
by 5 to 10% I will be using a power Venter so I should not have the problem of expelling the gasses of combustion
right? will condensing be an issue?
thanks
John
0
Comments
-
But .......
Why would you want to ?The G115 fire is not what I thought of as large......Watch the stack temperature.....0 -
hi ed because my load is 83,000 btu I don't want to have short cycling of my burner and i perfer not to go with another brand boiler i have my eye set on the buderus
thanks0 -
may end up with problems with
condensate, or other, by underfiring. You should not have short cycle problems with that big of a heat load, and you also need to include the dhw load, which could easily be bigger than this.
Using the right controls, w/ dhw priority, and/or optimizing the burner run cycle, outdoor reset, etc. (like Tekmar controls or Buderus controls), will help too.
Steve0 -
short cycle
If You want to extend the cycle length of the boiler than add a storage tank to the system , Ziggy has the digrams on his heating disk that will allow you to size 1 and how it will affect cycle lenth as per how large a tank you get .
Or look at the vitola boiler instead they have a much larger storage capacity to help reduce cycles0 -
short cycle
If You want to extend the cycle length of the boiler than add a storage tank to the system , Ziggy has the digrams on his heating disk that will allow you to size 1 and how it will affect cycle lenth as per how large a tank you get .
Or look at the vitola boiler instead they have a much larger storage capacity to help reduce cycles they start at 18.5 gal storage capacity0 -
i dont use indirect hotwater will i still be ok with my load and that boiler g115 model 28 my load is 83,000 btu
thanks
0 -
I looked into....
this w/ my boiler....frowned upon by Buderus. You can UPfire a 115-21...10%. Are you doing a power venter or the direct /balanced flue setup...kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
what do you
have for heat emitters?
Doesn't matter anyway your so close to the rating . I would leave it alone.
regards,
Robert
ME0 -
i am power venting0 -
watch the stack temperature
Removing baffles will increase stack temp. but you will loose efficiency. Call 1-800-BUDERUS.0 -
I Agree...
....your right there with the G115-28. Why over engineer the system. I would recommend the out door reset ....Not a great fan with a power venter unless no other option. I would direct vent .Alot less to go wrong with......... other then the Riello post purge control to worry about. I figured they have them ironed out by now...0 -
Why on earth.......
would you want to use a power venter when the Riello BF3 is available??? Think about it....no fan to clean, no motor to go bad,etc., etc....0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements