underfireing buderus
RoosterBoy
Member Posts: 459
has anyone had a problem underfireing a buderus g115 boiler
by 5 to 10% I will be using a power Venter so I should not have the problem of expelling the gasses of combustion
right? will condensing be an issue?
thanks
John
thanks
John
But .......
Why would you want to ?The G115 fire is not what I thought of as large......Watch the stack temperature.....0 -
hi ed because my load is 83,000 btu I don't want to have short cycling of my burner and i perfer not to go with another brand boiler i have my eye set on the buderus
thanks0 -
may end up with problems with
condensate, or other, by underfiring. You should not have short cycle problems with that big of a heat load, and you also need to include the dhw load, which could easily be bigger than this.
Using the right controls, w/ dhw priority, and/or optimizing the burner run cycle, outdoor reset, etc. (like Tekmar controls or Buderus controls), will help too.
Steve0 -
short cycle
If You want to extend the cycle length of the boiler than add a storage tank to the system , Ziggy has the digrams on his heating disk that will allow you to size 1 and how it will affect cycle lenth as per how large a tank you get .
Or look at the vitola boiler instead they have a much larger storage capacity to help reduce cycles0 -
short cycle
Or look at the vitola boiler instead they have a much larger storage capacity to help reduce cycles they start at 18.5 gal storage capacity0 -
i dont use indirect hotwater will i still be ok with my load and that boiler g115 model 28 my load is 83,000 btu
thanks
I looked into....
this w/ my boiler....frowned upon by Buderus. You can UPfire a 115-21...10%. Are you doing a power venter or the direct /balanced flue setup...kpc
what do you
have for heat emitters?
Doesn't matter anyway your so close to the rating . I would leave it alone.
regards,
Robert
ME0 -
i am power venting0 -
watch the stack temperature
Removing baffles will increase stack temp. but you will loose efficiency. Call 1-800-BUDERUS.0 -
I Agree...
....your right there with the G115-28. Why over engineer the system. I would recommend the out door reset ....Not a great fan with a power venter unless no other option. I would direct vent .Alot less to go wrong with......... other then the Riello post purge control to worry about. I figured they have them ironed out by now...0 -
Why on earth.......
would you want to use a power venter when the Riello BF3 is available??? Think about it....no fan to clean, no motor to go bad,etc., etc....0
- 120 Geothermal
- 394 Solar
