F&T Traps for one-pipe steam
Donald Lebnikoff
Member Posts: 9
I have a job where I need to put in a condensate pump for a building that is one-pipe steam. I would like to know if the correct way to size the F&T trap is by the total load of the system, because it is one-pipe steam.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=216&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=216&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Yes,
and you can split the load with parallel traps if that makes more sense.Retired and loving it.0 -
why do you
need to put in a condensate pump? just curious.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0