abandon coil
Chris_10
Chris_10 Member Posts: 14
If a domestic hot water coil is no longer being used should the coil be left open ?
Thanks.
  • Robert O'Connor_7
    Robert O'Connor_7 Member Posts: 688
    coil?
    Yes...Robert O'Connor/NJ
  • Ken_8
    Ken_8 Member Posts: 1,640
    Makes little difference
    I would however plug it.
    The reason? If it ever develops a pinhole - you'll empty the boiler water all over the floor and possibly dry-fire the boiler.
    Makes no difference whther water or steam. I would cap/plug it anyhow.
  • Chris_10
    Thank you!
  • Steve Paul
    Steve Paul Member Posts: 83
    coil -plugging
    if the coil has some resiual water in it and it is plugged. What will happen when the temperature in the coil is above 212 degrees? Steam can form inside the coil, without a pressure relief valve the coil could potetially explode. I was taught to puncture the coil from the inlet and outlet tappings before plugging it, or better yet, leave 2 open ends so that pressure can not build up.