On an exiting water boiler with no taps for updates can
the high temp limt and a low water cutoff be installed in
the supply line.
the high temp limt and a low water cutoff be installed in
the supply line.
0
Comments
-
.
when insurance inspectors call for manual high limit and low water on water systems we install a surface mount manual aquastat and cut in the piping near the boiler and install a tee ,add on a -low water cut off0 -
Yes
On a water boiler, the LWCO belongs ABOVE the boiler top, on our boilers. Others may be different.
The manual reset temperature limit can go there, as close as possible to the boiler outlet, too. There must be NO VALVES between the boiler and these controls.
Noel
Slant/Fin Corp.0 -
I don't think so
You want the high temperature sensor inside the boiler. If you install it on the piping and the pump stops, the sensor may not "see" the correct boiler temperature and you may get loss of life and/or property.
OK to mount the low water cut-off on the piping just so long as it's above the boiler.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements