Please don't do this!!! I didn't do this job but like to show this one to people. This is copper at its best.
prime example
of using zone valves vs. pumps, holy crap, that must have taken forever to solder. 15 or more zones, crazy. marc0 -
Isn't this a recycled picture?
Haven't I seen these before? For some reason I recall a very similar picture of a forest of copper being fed by a Buderus.
Regardless, I cannot think of a good reason for this sort of manifold madness.0 -
I wonder
How many GPM all those 007's are wheeling through that boiler when they are all on?
Think they need any additional heat in the boiler room with all that bare copper?
What would the amp draw be with all those circs up and running? 10-12 amps? Might as well run a 1 HP motor.0 -
BAD BUDERUS?????0 -
Maybe a poor choice of a phrase...
it just shows to go you that no mater what boiler you put in that the installer is the real key to a good SYSTEM.kpc
bad santa?????
Got milk ????? it is a joke, I like buderus ok,but this cust. blamed all his problems on the boiler to save money on the repair bill. We got it running for him but not able to fix the system. Yes I did show this before but I just can't help myself.........stay happy.......0 -
Not just the power consumption
but the amount of actual work being performed by 15 pumps consuming 78W each. 1170 watts to move 100,000 BTU, sounds like a forced air system with a strip heat running to boot
Be interesting to plot where all those pumps are running on their curves.
hot rod
Point well taken Joe
The picture should be titled "Bad Buderus Installation" or "How NOT to install a Buderus"!!
It's hard to find anything right about that job.
I would like to hear from you what effect an install like that is going to have on the 2107 and cycling the burner. Give us your take on that mess.0 -
Because the 2107 has condensate protection, the heat circuit (terminal 61 and 63 in the 2107) would be de-energized quite a lot during the first part of the burner cycle (hopefully the circulator circuit is tied into the R2107 terminals 61 and 63). I would also suggest turning the "Pump Logic"(condensate protection) setting from the factory setting of 104 to approximately 115/120. The boiler is the G215 series so thermal shock should not be an issue.
I think the share price of copper went up when this job was done!!0
- 86.7K THE MAIN WALL
- 56 Biomass
- 104 Chimneys & Flues
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 43 Industry Classes