Hazardous location radiant heaters?

Feed bagging site needing heat. Lots of fine air-borne dust.

Oil & gas not available, but electric is available. Must be explosion proof! looking for hazardous environment rated radiant panels.

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=98&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • Dale
    Dale Member Posts: 1,317
    Pads or HX

    Seems you could go with elect mesh pads under floor or wall or if more btu is needed an elect boiler with heat xchanger and std. pex or a fan coil(s) with warm air outlet.
  • Matt Clina
    Matt Clina Member Posts: 90
    Explosion Proof Heaters

    There are a bunch of companies that make XP heaters for chemical storage buildings, etc. This is just one of them:

    http://www.ruffneck.com/

    The dusty enviroment might pose more of a problem to the fans or fins though.

    You could always go with a HW or steam system with the equipment located outside of the hazardous area.
  • Carl PE
    Carl PE Member Posts: 203
    XP

    There are quite a few xp unit heaters available. Trane, Q-mark, etc..

    Not familiar with xp radiant panels, though.. Good luck with that.
  • BillW@honeywell
    BillW@honeywell Member Posts: 1,099
    Steam or HW system with pneumatic controls...

    Just put any ep/pe switches in a non-hazardous area, or in appropriate XP enclosure.
  • JimGPE_14
    JimGPE_14 Member Posts: 7
    Former salesman

    I used to sell Brasch electric heat, and even THEY don't recommend their explosion proof unit heaters. Convert the electricity to hot water via a boiler located somewhere else and heat with radiant floor, wall mount radiators or an air handler with a spark-proof fan and a hot water coil located out of the explosion hazard area and filtered well.

    Good luck!
  • Dave Yates (PAH)
    Dave Yates (PAH) Member Posts: 2,162
    tough conditions to be met

    These are railroad cars with wheels removed. Welded together with adjoining sides removed for open floor plan. Steel floor suspended in air. Steel walls & a steel roof too - brrrrrrrrrrrrrrrrr.

    No oil or gas available, or wanted for that matter.

    The floor is a no-go rock solid heat sink! Ain't exactly in great shape either!

    Toyed with the idea of electric water heater & hydropanels, but you'd have to see the fork-truck damage to walls to really appreciate how limited we'll be in locating panels. I haven't ruled that out completely yet, but Btu needs will be high. Side doors on the rail cars open for extended hours to receive and load product. Spring a leak with glycol-laden water & you've got an ample opportunity to poison tons of grain.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • shadro
    shadro Member Posts: 2
    Radiant heaters

    I am looking for an electric radiant heater for use in a recycle center. It must be suitable for use in a Class 1, Division 2 environment.
  • shadro
    shadro Member Posts: 2
    Radiant heaters

    I am looking for an electric radiant heater for use in a recycle center. It must be suitable for use in a Class 1, Division 2 environment.
  • SWEI
    SWEI Member Posts: 7,356
    the advice above still applies

    Hot water creates no ignition risk, so the simplest answer is still to locate the heat source outside the classified area and pipe the water to where heat is needed. 
  • Henry
    Henry Member Posts: 998
    Catalitic heaters

    There are several sour gas, propane and natural gas catalitic infrared heaters available for explosion proof locations. They are extensively used in the petroleum industry! Since yo do not have natural gas, you can use propane.