Water hammering
Bruce Rice
Member Posts: 2
i have a peerless hot water boiler with 4 loop zones and have had trouble with water hammering when the water is flowing though the zones. i have tried to bleed the system at various points with little success and had better success with putting hydronic cleaner formula 5 with silicone in the system. Do you have some advise for me? my boiler is in the basement and of course all the zones are upstairs which makes bleeding the system quite difficult. i've heard there is a product called an air scoop--do you have any information on this one? thanks brice
Bruce...
Is the pump on the supply or return? Where are the zone valves, supply or return? What kind of zone valves are they? Did this always happen? An air scoop is OK but a Spirovent is better. It sounds like the zone valves, and their placement/orientation with the pump and not the air scoop but having one will help with unwanted air....If it is air thats causing the banging it may be the water flashing (turning to steam) so you might want to turn the aquastat temp down.. Robert O'Connor/NJ0 -
water hammering
Robert, thank you for your help.
There are actually 4 pumps - one for each zone and they are situated on the supply side. There are really no zone values... (manual) they stay on... when the thermostat calls for heat, the pumps are engaged. The system is like 30 years old. Most of the hammering is in one zone. My idea now is put a 3/4" copper tube on the return side of worst zone with a bleed valve near the ceiling in hopes to get some of the air out. Acutally it may not be air that is the real problem???!?! Can you tell me more about a Spirovent?
Thanks.0 -
Bruce...
A Spirovent is a very effective air elemination device. If you install one on the supply, before the pumps and install an extrol tank to its bottom tapping and connect your makeup water connection between the spirovent and the tank, you have now made a pumping away modual. By installing a valve and drain set up on the return you can now force bleed your ill preforming zone of unwanted air. Check the bar to the left and click on books & more, there you will find a book called "Pumping Away" this will be all the info your ever gonna need about your air problem and solutions to your piping woes..Good luck!...Robert O'Connor/NJ0 -
flow chk valves
are there flow chk valves on each zone that hammering sounds like a stuck flow chk .Do you know if your system is a series loop or are some of the zones large and have a split supply and return if so you may have closed balancing valves or the flappers on the purge vales are closeed .What kind of convectors do you have baseboard or rads peace clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0
- 167 Indoor-Air Quality