Initial filling pressure on a gravity hot water boiler.
Markus_2
Member Posts: 2
I have a gravity hot water boiler (very old system) and had to drain it to remove radiators while refinishing floors in my home. When I refilled it it seems the reduction valve (which is rated for 12psi) doesn't work and the system fills to city water pressure (aprox 35-38 psi). The pressure gauge on the boiler is pretty simple, however it has the word "Danger" at the 30 psi line giving me a subtle hint that city water pressure is too high to run it at.What pressure do these typically run at? Any help would be appreciated. Thanks.
0
Comments
-
Fill Pressure
Yes the fill Valve is bad and needs to be replaced. 1 psi will raise the water level in the boiler roughly 2.34 feet. Generally preset at 12 psi from the factory, this will raise the water to 30 feet or so. Fine for most 2 story dwellings.0 -
Thanks Empire, guess I'll go drain some water out.0 -
think of it as flushing the system!
Marcus,
You've been steared correctly.
Since you need to drain the water again, why not take the opportunity to flush the system as well. You could add a cleaner (George seems to like Rhomer products!) or not, but open the valves wide and see if you can get some benefit from all the water going down the drain.
jerry
0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements