Hartford loop?
JM_2
Member Posts: 108
When mesuring for Hartford loop conection do you place the CENTER of the 1 1/4" loop at 2" below the normal waterline, or should the whole loop be 2" below. The Burham manual makes it look like the center of the loop is at 2" below.
( which puts 5/8ths of the loop above 2" and 5/8ths below 2")
Thanks
( which puts 5/8ths of the loop above 2" and 5/8ths below 2")
Thanks
0
Comments
-
2\"
If Burnham calls for 2" ,its the TOP of the loop that need to be 2" below the water line.Is your equalizer 1-1/2"? Not sure if any manufacturers call for 1-1/4". Check your minimum pipe sizes per spec.0 -
Equaliser is 2" but loop is 1 1/4"0 -
Here's some good reading and it can be found roght here on the wall
What you should know about Hartford Loops
Your friend in the industry,
Alan R. Mercurio
Oil Tech TalkThere was an error rendering this rich post.
0 -
;z4+2__0
-
REPLY??
Chris, who are you and how did this post happen. Something really weird just happened. The Chris post came through MY computor. What's up (b)..Robert O'Connor/NJ0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements