burnham power vent

Boston
Member Posts: 71
Does the fan on a burnham gas fired boiler with integral fan run continuosly, or should it only be running when the boiler is operating?
0
Comments
-
Constant fan or not?
Hello Brian. I saw a couple of threads here between you and Glenn Stanton and I thought I'd jump in. If it's the INPV model, the sequence is as follows: T'stat calls for heat, fan is energized, pressure switch makes, then ignition circuit starts. When call for heat has ended, fan goes off. It should not be running constant. Somethings up and should be checked out. Hope that helps.0