Vento indirect radiators
norfitz
Member Posts: 55
A San Francisco bldg has banks of Vento c.i. indirect rads in 9-section blocks stacked 3 blocks high, enclosed in ducting with huge squirrel cage blowers below. Old data shows 16 sq. ft. per section, but I believe that's a gravity airflow rating. As a tall convector cabinet uses more steam than a short one, it follows that these use far more steam when used as fancoils than their ratings suggest. Anyone know how to quantify this load? I've stumped a surprising sampling of well-known names with this one.
Thanks much,
Bruce Tompkins,
Power Boiler Sales
Thanks much,
Bruce Tompkins,
Power Boiler Sales
0
Comments
-
How about
Steam fan coil load in Pounds of Steam per Hour = CFM X Delta T of air (in degrees F.) divided by 800.
Can you work with that?Retired and loving it.0 -
Hi Dan. Are you saying I don't factor in the Vento's EDR ratings at all?
Bruce0 -
As you said
the rating you have is for gravity air flow. That formula will give you a way of checking the output for the purpose of boiler sizing when there's a fan blowing across the heaters.Retired and loving it.0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements