I'm wondering if check valves are needed on the supply side of the baseboard circuit if I put the zone valves on the return. This diagram is the basic plan with the exception of the zone valves on the return to hopefully reduce the tendency for them to bang when closing with more than one zone still calling. (yes installed in the right direction)
Any thoughts are appreciated.
Larry
Any thoughts are appreciated.
Larry
0
Comments
-
No
The zone valve will provide positive shut off and no gravity circulation can take place. Save the money on the check valves, they are not needed in this application.0 -
the check is a waste .
0 -
Zones valves slam for a reason. Some close with the flow and are more suseptible to slamming. Either way it sounds like a velocity problem. Is the pump too much for the system?0 -
the pump
is a Taco 007 and the valves are Honeywell V8043E. Will there possibly be an improvement in slamming when I change to pumping away and locating the valves on the return?
Larry0 -
Can I ask if the slamming is more prevalent when only one zone is calling for heat?0 -
no real difference
the system has three baseboard zones and an AQ475 reset controller. If I take off one spring on the valves there is no slamming. As long as the circulator is running, when a zone closes with both springs, it bangs. I think the original setup back in 1962 had slow acting motor open/motor close valves. Thanks for your input.0 -
You might try
a pressure differential bypass valve.
cheese0 -
banging
an air chamber or shock arrestor will eliminate any banging due to any quick closing valve be it a zone valve or flushometer0 -
.
its pretty common pratice where i am to remove 1 spring of the zone valve0 -
Just Curious
Since the drawing you posted is really that of Honeywell as indicated on their web site for the AQ475 control, this setup should work as intended. But this drawing does not show the expansion tank or air elimination device. Where is your expansion tank and what static fill pressure are you running?
Glenn Stanton
Burnham Hydronics0 -
very perceptive
Glenn,
A little more background. The Weil Mclain HE series 2 boiler has a built in air separator with a tap at the top of the sections which goes to the compression tank. With the circulator on the return, air has always been an issue and I have maintained a rather high static pressure of about 20 lbs. in an attempt to keep the air from coming out of solution. The hope is that when the piping is changed to reflect the Honeywell drawing, and with larger headers etc., multiple problems will be solved including the cavitation issue on the indirect DHW tank circulator (that is a separate issue and thread).
For some backround you may check this thread that dealt with the cavitation issue.
http://forums.invision.net/Thread.cfm?CFApp=2&Thread_ID=16744&mc=11#Message104878
Thanks for your interest and any input is greatly appreaciated.
Larry0 -
Gravity flow is possible in a single pipe
It happens! A positive shut off zone valve will stop flow through a pipe, but cannot stop flow within a pipe. Hot water flows to the top of the pipe and cold water settles to the bottom. With this temp difference flow is created in a single pipe. Add a few radiators or convectors and you can get alot of heat off a zone with a zone valve is shut off. Doesn't happen always, but it does happen. I believe the old gravity one pipe hot water systems operated completely based on this principle. STeamhead and a few others have seen these systems I believe.
Check out the old B&G manuals...flow checks on both supply and return. This may look like a way to sell more product, but there is sound theory and experience behind it.
Boilerpro0 -
I would
use a Grundfos 15-58 on speed one for the heat. Speed 3 for quicker DHW recovery on the indirect circ. 15-58's have an intergral check to prevent ghost flow as B-pro mentioned. Same price as a regular 15-42, by the way. Why not use them and take that potential out of the equasion?
And I would still move the ZVs to the return side.
The banging may be improperly supported pipes and hard to correct. Proper flow velocity and good zv placement will help.
This article deals more with causes and cures for ghosts in the pipes
hot rod
http://www.pmmag.com/CDA/ArticleInformation/features/BNP__Features__Item/0,2379,13972,00.html
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements