boiler question
rick_16
Member Posts: 5
Just received oil boiler weil mclain 170000btu output .What can I do to drop the output to around 125000,btu. Any suggetions .
0
Comments
-
Just received oil boiler weil mclain 170000btu output .What can I do to drop the output to around 125000,btu. Any suggetions .0 -
Piece of cake, cake, cake...
Change the end cone on the bruner for the desired firing rate and put the nozzle size of your choosing in it (downfiring). Be aware a 1.00 GPH nozzle only puts out 1 GPH when at 100 # pressure. W/M and most makers are using well over 100 # in many instances.
Be careful and perhaps call 1-800-oil-burn.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
weil boiler
You didn't mention which boiler you have, but look at the firing rate. You can drop it to about 65% of rated firing rate and still have good efficiency, but be careful. Are you using a steam boiler or hot water. Being a Weil, you can easily remove a section or two if needed, but you'll need a new jacket. Talk to your local Weil rep...that's your best bet. But why is the boiler too big???
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements