I'm figuring a snowmelt job in the Chicago area. 3/4" PEX 50% glycol 150 btu /sq ft. Total area about 3200sq ft. What loop lenghts will be best? Thanks for your help
0
Comments
-
Snowmelt
Why use 3/4 pex? depending on the application; you should be able to use 1/2 or 5/8 pex. I would run 300' loops.0 -
5/8 PEX
Is a good bit easier to lay down for sure. If you go ahead with the 3/4" here are some figures.
3200 sqft x 150 btu/sqft = 480,000 btu
25f delta T = 38.4 gpm
8" oc spacing
18 loops at 290 feet using 50% glycol = 13 ft/hd
Supply water temp = 137f Required surface temp = 36f
Tim D.0 -
If I did use 5/8" PEX what should my loop length be?0 -
21 loops
at 250 feet, 8 inches on center. This bumps your ft/hd to 14.5
Tim D.0 -
will go with Tim on this
With one slight difference. In the pex manual it state's to use 6" loops for a high traffic area IE Hospital walkway's, old folk's home. Use 9" loop's in medium use issues, IE store front's, apartment entrances and to use 12" loops for residential. I would stick with the 5/8 pex though. I don't believe you would succeed with 1/2. I personally use the 9" loops..:)0 -
Snowmelt
We use 3/4" at 9" OC 300' loops. For snowmelt we usually use pex-al-pex. It has a larger ID than pex. We are south of Buffalo NY. We do get some snow here and everyone that we have done works great.0 -
And You'd
0 -
Just a thought
Spacing is basically a function of desired output vs required water temperature.
Tim D.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements