Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Heat Loss
Bill_31
Member Posts: 6
Here we go again... My plumbing manager insists that it is more important to measure existing radiation when installing a replacement hot water boiler. I am of the school that you should complete a manual J on the house. Your thoughts?
Thank you.
Thank you.
0
Comments
-
You're both right!
A heat loss will tell you what is TRULY needed. An EDR will tell you what's there. Interpolate between the two and with some form of reset or water temperature control device you can both be right!0 -
You're both right!
But you're a lot "righter" than he is (:-o)
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements