Bill at Honeywell or anyone else that wants to chime in:

This looks like a Honeywell zone valve (couldn't find a model number) that's operated by a line voltage thermostat; all the wires have been disconnected (5 wires) and the owner wants me to get it back in operation.

No problem except do you see those two wires coming out of the box behind the zone valve? When the thermostat is turned on, I get 110 volts out of each wire (1 meter lead on the wire and the other meter lead on the box which I'm guessing is grounded).

Any ideas?

What I'm thinking about doing is removing the old zone valve and replacing it with a 24 volt zone valve and installing a controller (like a Taco SR501). I'm just a bit put off by 110 v. out of each wire.



<A HREF="http://www.heatinghelp.com/getListed.cfm?id=53&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • oil-2-4-6-gas
    oil-2-4-6-gas Member Posts: 641
    .

    .what voltage do you get when you check both wires together//110 ,220 or nothing
  • Weezbo
    Weezbo Member Posts: 6,232
    is .

    there are new heads and some new valve that screws into the body..pretty sure its a 1960's model honeywell:) look on the transformer has a run date on it that number tells you the year....65 66 67 like that... The transformer numbers i almost can read i am just not good at computer stuff:( if you enlarge the photo..maybe you can get one new replacement head and all is cool:)
  • Voltage

    at both wires is zero. Seems too weird and will make another trip to clarify.

    Weezbo: that closet is too small for both my head and a flashlight; I will have to remove the zone valve to see any numbers.

    Alan

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • David_5
    David_5 Member Posts: 250
    Just install a transformer

    Wire 115v to primary and secondary to the new 24V zone valve. I can't explain the two hots into the box. I think you need to find out where the wire comes from.

    David
  • Glenn Harrison_2
    Glenn Harrison_2 Member Posts: 845
    Is it possible that...

    one wire goes to the thermostat and one comes back fromthe t-stat??? So white is not neccesarily common/nuetral?
  • Weezbo
    Weezbo Member Posts: 6,232
    those old valves are Heavy...

    the new things they use to update them are made of Plastic:))) somethings Never change:) the new test meters weigh in like 2 and a half ozs the old Bacharac... or worse yet, Lynn... you see:) nowadays i bet they could spin out two three new Japaneese cars outta ten honewelly zones valves from the 60's and a couple old 8&1/4" skill saws:) and one of the Original HOLE hoggs:))) oh that closet does seem like an ideal place to practise changing zonevalves out while standing on ones ear:) should be a new Olympic event...:) buncha plumbers trying to sort out a zone valve while standing on one ear:)))
  • BillW@honeywell
    BillW@honeywell Member Posts: 1,099
    I've been away for a couple days...

    so I just got this. That is a very old product, and has no direct replacement. It's a line voltage system, and those oddball leads may have gone to another piece of equipment. You can replace it with a conventional V4043 series line voltage zone valve in 1/2,3/4 or 1" sizes, sweat,flare or NPT. There are a couple of stat options, T451 or T651. This will give you two position control (on/off). If you need or want proportional control, you'll need a commercial type V5011 with a direct-coupled actuator, and appropriate stat.
  • Tom Hopkins
    Tom Hopkins Member Posts: 554
    Bad Neutral

    It sounds to me like the neutral wire is open if that's a 120vac circuit.

    If the neutral wire is open you will read 120 volts back through the coil/motor or whatever is being controlled. Trace the neutral circuit out back to the panel. I'll bet it's open somewhere.

    I've gotten bit by open neutrals on a couple of occasions.
  • oil-2-4-6-gas
    oil-2-4-6-gas Member Posts: 641
    /

    i would say the same if the nuetral is bad you will feedback and get 110 on both but zero -lead to lead or someone switched a wire somewhere and you have 110 on both -- of the same phase//trace them out replace and hook up another zone valve