flow check
cool
Member Posts: 3
my sister is remodeling her house so i got stuck doing the air and heat, I am putting the circ on the outlet of the boiler and wanted to know if i can put the flow check before the circ and on the outlet of the boiler. it is a 5 zone system and zone valves on return.
Flow check
Circ. on the supply side.....called pumping away. Flow check goes after the circ.. You might want to dig a little deeper because I belive you will also need a back flow preventer to prevent the heat from backing up to the last
room. (Watts 9D or combo) if your in Massachusetts it's
code.0 -
flow checks
If you are using zone valves, you won"t need any flow checks at all. The flow check is there to prevent convective circulation and over heating. A closed zone valve will stop any unwanted circulation. If you did not have zone valves, then you would need to have a flow check on every zone.
The backflow preventor is to protect the potable water supply from contamination from the boiler, it has nothing to do with heat flow.0 -
Steve,
No chance of back heating the last rad' without a back flow preventer on the return (end of loop) at the boiler? Portable water supply?0 -
Nomenclature
Dan, it sound like you are refering to a flow check placed at the return end of a zone - perfectly good application. The backflow preventer (9D etc) is typically applied only to prevent a reentry of boiler water to the potable supply and not substituted for either a spring check, swing check or flow check in the system piping. Enjoy.......Dan
Thanks!!!!!!!0