Why must i use a jumper when it is put on a boiler and not when its on a furnace someone was trying to explain it to me the other day I got side tracked and didnt really get it?
0
Comments
-
the Primary?
relay wont "MAKE". burner no mojo.0 -
On most boilers .......
the thermostat or end switch etc. connects to the TT terminals of the aquastat which on a call for heat sends 120 volts through the limit circuit to the primary control.Without a jumper you won't complete the relay circuit which starts the burner.
On a typical warm air furnace the primary control has 120 volts constantly and the thermostat connects directly to the primary control which on a call for heat makes contact across the relay circuit hence no need for a jumper.
I highly recomend Carol Fey's books on electricity and controls available for purchase on this site.
John0