Old honeywell zone valve wireing
Don Baker
Member Posts: 23
I was sent on a job to wire up some old honeywell zone valves that I have never seen in my life before, there was no model number or wireing diagram...
The valve was big and clunky (24v) and looks to have an incorperated end switch. 5 wires... 1 white, 2 black and 2 red. I did manage to get the valve to open but it did not spring return so I am assuming it should be power return. Seems odd because they are run by a 2 wire thermostat.
If I powered up the 2 blacks the valve looked like it was opening properly, if I powered up the white and black the valve just kept rotating.
Unfortunatly the plumbers removed the wireing for a reno now it's up to the electrician to figgure out how they work. Any one know these beasts?
The valve was big and clunky (24v) and looks to have an incorperated end switch. 5 wires... 1 white, 2 black and 2 red. I did manage to get the valve to open but it did not spring return so I am assuming it should be power return. Seems odd because they are run by a 2 wire thermostat.
If I powered up the 2 blacks the valve looked like it was opening properly, if I powered up the white and black the valve just kept rotating.
Unfortunatly the plumbers removed the wireing for a reno now it's up to the electrician to figgure out how they work. Any one know these beasts?
0
Comments
-
Without a base number this could be hard,
if you can find one go here, it's THE place to start.
http://hbctechlit.honeywell.com/0 -
Don, I have the wiring diagrams
and the specifications for those zone valves.
e-mail me at gastc@cox.net and give me a Fax number and your mailing address. I will fax diagrams and will mail specs in postal mail.0 -
Don has disappeared
Oh well this goes on all the time here on the Wall. Ask a question and then disappear. I will try to e-mail Don to see if I can help him out.
For those who may be wondering the Zone Valve he had is a V-8031 Honeywell Zone Valve, yes it uses a two wire series 80 thermostat. There was a comparable model back in those days the V2031 which used a three wire thermostat.
The 8031 is powered open and springs closed on more close observation it may be noted that terminals are labeled "W" "B" and "Y" Thermostat goes to W & B and the transformer is wired B to Y. The remaining two terminals are the end switch which go to "T" "T" on the relay.
The V-2031 was a power to open power to close model.0 -
Don hasn't disappeared
Sory Folks and thanks, I just went AWOL for the weekend to an antique motorcycle ralley. Business as usual tomorrow.
Tim I would apperaciate a fax of the wireing diagrams you spoke of, I will send the fax # to your email. Thanks again for all your help.
Don0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements