gravity conversion
Options
R. Kalia
Member Posts: 349
I read the article on gravity conversions and flow rates:
http://www.heatinghelp.com/newsletter.cfm?Id=125
But if I want ΔT=20, the flow rates listed for gravity conversions are way too high. I calculated this using the specific heat of water, see below and please check if possible.
My house was designed for around 160,000 BTU, so the chart says 25 gpm for a gravity conversion. Water specific is heat 8.34 BTU/gal/F. So heat delivered = 25*8 BTU/minute/F = 12,400BTU/hour/F. so [B]ΔT = 160,000/12,400 =13F[/B].
Further, for the [B]actual[/B] BTU needed on a design day (only 80,000 because of insulation), I would have ΔT=6.5, which is wasteful and would reduce efficiency in a condensing boiler.
The article says people have flow rates that are too high, but I claim the flow rates listed in the article are too high. The flow rates for 'modern' systems give a better number but it is still less than 20F. And as I said, if the actual BTU is much lower than the design BTU, the ΔT is even smaller.
http://www.heatinghelp.com/newsletter.cfm?Id=125
But if I want ΔT=20, the flow rates listed for gravity conversions are way too high. I calculated this using the specific heat of water, see below and please check if possible.
My house was designed for around 160,000 BTU, so the chart says 25 gpm for a gravity conversion. Water specific is heat 8.34 BTU/gal/F. So heat delivered = 25*8 BTU/minute/F = 12,400BTU/hour/F. so [B]ΔT = 160,000/12,400 =13F[/B].
Further, for the [B]actual[/B] BTU needed on a design day (only 80,000 because of insulation), I would have ΔT=6.5, which is wasteful and would reduce efficiency in a condensing boiler.
The article says people have flow rates that are too high, but I claim the flow rates listed in the article are too high. The flow rates for 'modern' systems give a better number but it is still less than 20F. And as I said, if the actual BTU is much lower than the design BTU, the ΔT is even smaller.
0
This discussion has been closed.
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements