gravity conversion
                
                    R. Kalia                
                
                    Member Posts: 349                
            
                        
            
                    I read the article on gravity conversions and flow rates:
http://www.heatinghelp.com/newsletter.cfm?Id=125
But if I want ΔT=20, the flow rates listed for gravity conversions are way too high. I calculated this using the specific heat of water, see below and please check if possible.
My house was designed for around 160,000 BTU, so the chart says 25 gpm for a gravity conversion. Water specific is heat 8.34 BTU/gal/F. So heat delivered = 25*8 BTU/minute/F = 12,400BTU/hour/F. so [B]ΔT = 160,000/12,400 =13F[/B].
Further, for the [B]actual[/B] BTU needed on a design day (only 80,000 because of insulation), I would have ΔT=6.5, which is wasteful and would reduce efficiency in a condensing boiler.
The article says people have flow rates that are too high, but I claim the flow rates listed in the article are too high. The flow rates for 'modern' systems give a better number but it is still less than 20F. And as I said, if the actual BTU is much lower than the design BTU, the ΔT is even smaller.
                http://www.heatinghelp.com/newsletter.cfm?Id=125
But if I want ΔT=20, the flow rates listed for gravity conversions are way too high. I calculated this using the specific heat of water, see below and please check if possible.
My house was designed for around 160,000 BTU, so the chart says 25 gpm for a gravity conversion. Water specific is heat 8.34 BTU/gal/F. So heat delivered = 25*8 BTU/minute/F = 12,400BTU/hour/F. so [B]ΔT = 160,000/12,400 =13F[/B].
Further, for the [B]actual[/B] BTU needed on a design day (only 80,000 because of insulation), I would have ΔT=6.5, which is wasteful and would reduce efficiency in a condensing boiler.
The article says people have flow rates that are too high, but I claim the flow rates listed in the article are too high. The flow rates for 'modern' systems give a better number but it is still less than 20F. And as I said, if the actual BTU is much lower than the design BTU, the ΔT is even smaller.
0                
            This discussion has been closed.
            Categories
- All Categories
 - 87.2K THE MAIN WALL
 - 3.2K A-C, Heat Pumps & Refrigeration
 - 59 Biomass
 - 427 Carbon Monoxide Awareness
 - 118 Chimneys & Flues
 - 2.1K Domestic Hot Water
 - 5.7K Gas Heating
 - 113 Geothermal
 - 164 Indoor-Air Quality
 - 3.7K Oil Heating
 - 73 Pipe Deterioration
 - 1K Plumbing
 - 6.4K Radiant Heating
 - 393 Solar
 - 15.5K Strictly Steam
 - 3.4K Thermostats and Controls
 - 56 Water Quality
 - 51 Industry Classes
 - 49 Job Opportunities
 - 18 Recall Announcements