Steam Pipe Insulation-Where to get it?
Mark K
Member Posts: 26
Hi all,
I just bought a new house with a one-pipe steam heating system. The pipes in the un-heated basement had damaged asbestos insulation on them, so I had that removed.
Now, I want to re-insulate them. What type of insulation should I use? The pipes are all different sizes; is there a pipe wrap available so I don't have to measure it all? All the insulation I've seen in Home Depot says not to use on Steam pipes.
Thanks for the help!
I just bought a new house with a one-pipe steam heating system. The pipes in the un-heated basement had damaged asbestos insulation on them, so I had that removed.
Now, I want to re-insulate them. What type of insulation should I use? The pipes are all different sizes; is there a pipe wrap available so I don't have to measure it all? All the insulation I've seen in Home Depot says not to use on Steam pipes.
Thanks for the help!
0
Comments
-
Use something like this
http://www.knauffiberglass.com/index.cfm?fuseaction=prd.dspProdDetail&ID=1
It won't be in a home center, though.
Noel0 -
If you have a local plumbing/heating supply store they should have pipe insulation. You want to get the fiberglass kind. You may want to wrap a string around the different size pipes and bring it to the supply store and they can tell you the size. The fiberglass insulation comes in 3 foot lengths, so you need to measure the length of the pipes as well.0 -
.....in Central Jersey
State Insulation (732)-442-5656.0 -
Pipe Insulation
The string measurement method works fine in a pinch, but where would I be without my Pocket Rocket (R) available from Dan's site? Measures anything cylindrical up to about 16" diameter, and it is accurate.
For insulation, the advice about moulded fiberglass (Knauff, Certain-Teed, Owens Corning or J.Manville) is the way to go. Do NOT use foam products; generally not made for those temperatures and will melt.
Your local energy code may dictate thicknesses to be used. Buy the thickest you can afford, forget the 1/2" thick stuff you find in the home centers. For thicknesses here in Mass., they start at 1.5 inch thick to 1.5" pipe and use 2 inch thick for pipe sizes up to 4 inch. So if 2 inch pipe, 2 inch insulation is the way to go (legally speaking).0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements