one pipe

jamie_2
jamie_2 Member Posts: 4
My friend just bought a module home and we're doing the heating system hook up in it. He has 60 ft of 3/4" fin tube radiation and 750ft of 1/2 pex in floor in basement. We also want to hook up a boiler mate. The home manf. recommends a Weil Mclain ag4 boiler but didn't give a btu size. Also if we go with a one pipe system what size of line should we run to tie in the baseboards with. I know we'll have to do primary/secondary piping for the in floor. Your help would be appreciated. Thanks.

Comments

  • ScottMP
    ScottMP Member Posts: 5,883
  • Ken_8
    Ken_8 Member Posts: 1,640
    You may be refering to a

    Weil McLain CGa-4 ?

    If so, the CGa-4 seems like gross overkill on a modular contemporary (implying well insulated) home, but would have an input of 105MBTU's and a net I=B=R output of 77MBTU's.



    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Jim Erhardt
    Jim Erhardt Member Posts: 52
    Heat loss calc

    The only way to properly size the boiler is to do a heat loss calculation. Based on what you have told us, a 105,000 BTU boiler would in all probability be overkill. Avoid over-sizing the boiler.

    If you connect the baseboard as a series loop, one zone with 3/4" copper, you will need a pump with a slightly higher head capacity, such as a Taco 008 or Grundfos 15-42. If you go with two zones and zone valves, a Taco 007 should be just fine.

    Your 750' feet of 1/2" PEX in the basement slab should be divided into two loops, and piped as a separate zone with its own circ and mixing valve.

    Your indirect would be yet another zone, preferably with its own circ for maximum output. Consider using a priority relay.

    Please feel free to download our latest heat loss software to be sure you are sizing the boiler correctly. You can download our Hydronic Explorer 2 software (for free) from here - www.slantfin.com/he2

    Good luck!
  • Weezbo
    Weezbo Member Posts: 6,232
    how many square ft is the modular?

    does it have 6 foot sliding doors,are there cathedral ceilings,is the pex in 1 2 3 4 loops what you have with a package home is a variety of vagarities.you need actual carpenter ,electrician,plumbing heating guys on the job. a guy with a hammer another with some linemans and another with a wrench isnt going to do right by you. sight unseen,advise is apt to be a case of too many chickens spoils the broth:)) I have no reason to lie. I am telling you the truth.
  • jamie_2
    jamie_2 Member Posts: 4
    one pipe

    The module home is 55x25 and the upstairs has 60 ft of 3/4" fintube radiation. The basement has 750ft of 1/2 pex in four circuits. He wants a 40gl indirect water heater also. You say i'll have to go to a Taco 008 pump for the radiation if i go one pipe 3/4 inch. What would you recommend for a boiler if not a cg4 as stated by the home manufacturer. Would i be better off with a cg-3.Thanks for your input.