Oil burner piping?

laundryman
laundryman Member Posts: 1
I am a contractor from pittsburgh helping my sister on a long distance job in NE Baltimore. Her existing system is a Burnham RS/110 boiler with CI rads. We are adding two zones of copper BB fed with 1/2" PEX. After checking Burnham's site they reccomend circ. zoning without P/S loops. Will there be enough flow through the boiler if only one BB loop is calling?
In pgh. I never deal with oil and I don't pretend to know anything about it. But I would like someone to check out her oil burner. Anyone close?

Comments

  • Don_44
    Don_44 Member Posts: 12


    With a 20 degree temperature drop you can send about 14,000 btu's through a zone using 1/2" pex. If you are using conventional baseboard that is about 20' of board, that will usually heat about 300-400 square feet of living space. Hope this helps.
  • Robert O'Connor_6
    Robert O'Connor_6 Member Posts: 299
    go to the

    "Find a Professional " bar at the top of the page type in your zip code for Baltimore.

    Steamhead is a great resource near you. I think his firm is out of Towson MD

    Regards

    Robert

    ME
  • Steamhead
    Steamhead Member Posts: 17,514
    Here I am, LM (thanks, Robert)

    this job sounds like it's right up our alley. Give us a call at (410) 821-3997. The voice mail is on if we're not in the office, and we check it several times a day. Or you can e-mail me.