steam main vents

Nate Perkins
Nate Perkins Member Posts: 8
I am quoting a replacement steam boiler in an old house. (Taking out old Timken oil fired boiler).
Customer complains of uneven heating

Currently, steam main vents are at the end of 3/4" dry (above water line) condensate return lines at back of boiler.

Ends of 2" steam mains have been drilled and tapped in the side and a 1/8" air vent installed vertically.
I am considering installing 2" x 1/2" Tees 15" back from ends of mains for new Steam vents

Question: Are existing vents at drop in condensate return adequately removing air from main? Or am I on the right track?

Comments

  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    I'm no expert....

    but sounds like they used radiator vent instead of main vents on the main....that won't do...you are on the right track. kpc

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Steamhead
    Steamhead Member Posts: 17,513
    To answer your question properly

    I'd need to know if this is a one-pipe or two-pipe system. If two-pipe, are there air vents or traps on the radiators?

    Then I can tell you where the vents should go, and how to size them.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Nate Perkins
    Nate Perkins Member Posts: 8
    One Pipe

    Sorry, I left out the most important part.
    System is a one pipe, I know that the proper point for main vents is 15" back from ends of runs.
    And I am prepared to put them there if necessary.
    But.... When I am standing in the basement and imagining the interaction of steam, air, and condensate I am wondering if those large vents on the ends of dry returns are not functioning to remove enough air so as to make cutting into those 2" mains an expensive exercise with little real value to the consumer?

    My first reaction is that once condensate reaches the ends of steam mains and starts to fill returns then there is no place left for air to move back toward vents. (also, the air will probably not move willingly down the pitched 3/4" condensate returns).

    I almost think that putting them there just allows steam pressure from the boiler to drive water back up the returns.
  • Steamhead
    Steamhead Member Posts: 17,513
    How Long

    are your steam mains, and whar size pipe are they? Also, how long are the 3/4" dry returns from the steam main connections to the vent locations?

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Nate Perkins
    Nate Perkins Member Posts: 8
    Pipe Sizes

    Thanks for responding:

    Steam mains are piped in an "H" pattern with boiler at the center of "H". From steam riser on boiler to each leg of H is approx 20-25' developed length of 2" steam main with an equal amount of 3/4" back to steam vent.

    Total standing load is 356 sq feet of mostly column type radiators with 1-1/4" run-outs to rads.
    Largest singlw rad is 56 sq ft.