vaporstat substitute
T. Riley
Member Posts: 26
I have found a new surplus Mercoid PG-3-P1 pressure switch. Range is 1-30" WC. Mercury switch opens on pressure rise. Can anyone think of a reason why this would not be an acceptable substitute for a vaporstat?
0
Comments
-
it should be a perfect fit..
1 3/4'' = 1 ounce..mercoid was a division of american radiator company.. 'course it might look really nice on the shelf of your personal heating museum if you have one.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Tom, make sure
that it doesn't mean 1-30 inches of vacuum. If so, it was designed to control a vacuum pump on a vacuum-return system, and won't operate on 1-30 inches of pressure.
E-mail me the link and I'll have a look.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Considering we buy vaporstats for
~$110, I'm not usre the "savings" will offset the potential liabilities!
If you leave a plain-jane 404 in as well (in series), then I would use it in a heartbeat.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
My feelings as well
Most times when you think you found an inexpensive shortcut, you don't. Unless you have time to experiment, I'd stick with what we know works. Mad Dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I've seen Tom's system, guys
a beautiful Hoffman Vapor! He will be keeping the present PA404 as a backup.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
if i'm not mistak'en
mercoid controls were a top of the line product in their day.. he should be fine..some of our customers have boilers with these vintage controls still functioning and doing it well..still it would look really handsome mounted on a wall like a trophy.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
I didn't even know they were still made
Dwyer Instruments owns the brand now. Thanks, Tom!
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
i didn't know that either..
i thought they were a thing of the past..interesting..gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements