Hey all you Wallies (with more vast experience than me with residential oil-fired boilers) ...... What's your preferred barometric damper and why? It seems like some dampers (no names mentioned) I have seen lately have some real issues: 1) they seem to corrode fairly quickly; 2) they have alignment problems, get stuck, and don't swing freely; 3) they make noise when shutting against the stop; 4) the pivot pins wear through; 5) the pivot saddles wallow out; 6) they have a pretty funky counter-weight mechanism. As all you oil-heads know, it's a real drag when the draft gets off-spec due to any of the issues above. Combustion efficiency spirals down into the tyvek suit and soot mask abyss! Does anyone out there make a good long-term damper? Seems like it would be well worth it to spend good money on a damper that was robust, kept the draft at the proper setting, and mimimized the aromatic blackness of the nuisance service calls we have all experienced. Thanks in advance for any input you might have here.

Comments

  • J.C.A._3
    J.C.A._3 Member Posts: 2,980
    Field, Hands down!

    Not those cheesy ring and gate jobs but the real ones. Only time I've replaced them is when I put in a new heater. The barometrics supplied with the boilers, lately (read...Effical) are a very noisy product IMHO. I've gotten to the point where I order the Fields as an add on automatically. One thing, the installer MOST DEFINATELY needs to know the difference between vertical and horizontal! Can't count how many I've found in the wrong slot. Chris
  • I like the brand

    that Burnham used to ship with each V8 boiler . I think it is Field or Effikal . They stopped shipping them , so we're back to the flat black ACME special .
  • Robert O'Connor_6
    Robert O'Connor_6 Member Posts: 299
    Tjerlund

    It's even got slots to put your screws in to the flue pipe.


    "Series A
    This single acting deluxe unit is made of stainless
    steel for low maintenance and corrosion
    resistance. It has integral anchor points and self-
    aligning, self-centering rocker bearings for long
    lasting service. A cushioned stop minimizes rattle
    and noise. Adjustment is easily accomplished by
    moving counter weight on outside tab."

    Priced competively

    Robert

    ME
  • Bob Knebel
    Bob Knebel Member Posts: 26


    Howdy J.C.A. ..... Thanks for the quick reply! Any chance you could give me a model number / type for the Field damper you prefer. The Type M has been OK but if there was something better, I think the money would be well-spent. Thanks again ... Bob
  • J.C.A._3
    J.C.A._3 Member Posts: 2,980
    Bob,

    The RC model. They come with a pile of parts to cut them into a piece of pipe, but with a bit of crimping across the top half, they fit into a manufactured tee.(6-7" has apparently shrunk....good news for guys!:^) ). Chris
  • Bob Knebel
    Bob Knebel Member Posts: 26


    It's me again. I heard from someone that Weil McLain used to ship (and maybe still does) a nice stainless barometric with a rubber bumper stop with their oil-fired boilers. Is this true? Anyone know anything about these dampers? Manufacturer? Info? Thanks for any help you folks can give me.... Bob
  • Yes , they still do

    for every Gold oil boiler , it's in the trim package . And I'm almost positive it's Effikal .
  • Robert O'Connor_6
    Robert O'Connor_6 Member Posts: 299
    That sounds like

    the Tjerlund Try it you will like it!!

    I am a service person/installer no affiliation!!

    Robert

    ME
  • J.C.A._3
    J.C.A._3 Member Posts: 2,980
    See....

    Effical. I wasn't at all impressed with them. The Field just seemed to be a superior product IMO.The Effical units seemed , to me, to rattle quite a bit more than the Field units.The holder of the pins in the sides of the unit were straight cutouts and not V shaped like the Field units.Seemed to make them slam "outward" on startup, and the bumper plastic would absorb a bit of it, but not all. Consider the flue pipe as a "boom box", which it effectively becomes. The E unit , on start-up would slam the sides of the damper into the face of the mount, and seemed to be noisier to me anyway.

    Pre and post purge controls have helped the slamming to be lessened but have not made it disappear completely. Like almost everything else in the field, I find this particular product to be at the top of my list. Again, JMHO. Chris
  • Robert O'Connor_6
    Robert O'Connor_6 Member Posts: 299
    Did ya ever try

    a Tjerlund or have you seen one Chris?

    Fields has a good product also

    I like to put them in a tee right at the chimney and this helps with noise also.

    Regards,

    Robert

    ME
  • Bob Knebel
    Bob Knebel Member Posts: 26
    Hey Thanks Robert and Ron Jr!

    I will definitely look into Tjernlund. We have had good luck over the years with their power venters (not in oil service) and "fans-in-the-cans" for combustion air. I'll talk to the Tjernlund and/or the W-M rep here in Montana to see what I can find out.

    Bob Knebel / Radiant Engineering, Inc.
  • J.C.A._3
    J.C.A._3 Member Posts: 2,980
    Robert,

    Haven't seen one yet, but the oil fired units I've installed lately always have the Fields in seperate boxes.(my choice) The latest ones I saw with Viessman were tossed, (6" units going into a 7" pipe, no thank you) We tend to use the same chimney's far more than I would like, but that usually comes down to the situation on a new install.(always measured and inspected, to cover my butt!)

    I will give a look/see at the Tjernlund units. Haven't come across one yet, but will look at them with "my minds eye" open, and decide. Thanks for the input. Chris
  • Robert O'Connor_6
    Robert O'Connor_6 Member Posts: 299
    Oh Chimney's

    There is a real can of worms. Are they putting miles of slinky's in chimney's across Mass too?

    i have to winder how long they are gonna hold up. Someones in for a bad nite call!

    Regards

    Robert
  • Weezbo
    Weezbo Member Posts: 6,232
    Field

  • Jack_23
    Jack_23 Member Posts: 153
    FYI...NFPA 31 committee

    Is discussing eliminating the "requirement" for a barometric on every unit.
  • Robert O'Connor_6
    Robert O'Connor_6 Member Posts: 299
    Jack

    are you on the committee?

    I think the manufacturer should be able to dictate. I actually think they already have that option if they spell it out in their I/O manuals?

    Thanks

    Robert

    ME
  • JaredM_3
    JaredM_3 Member Posts: 12


    The Field model RC has always been the most reliable. The Field model that ships standard with many oil boilers is a cheaper alternative. The Effikal stainless model is also very good. I have found the Effikal is a bit noisy on some boilers, especially the Weil McLains.

    Proper placement of the draft control is important, the instructions are very specific on their replacement...but who reads them anyway?

    -Jared
  • Dave Palmer_3
    Dave Palmer_3 Member Posts: 388
    but

    they stopped shipping the collar so you have to buy a tee
  • Jack_23
    Jack_23 Member Posts: 153
    Yes, I am

    With the changes in technology and system design, I think it's time to give "system design flexibility" to the manufacturer. this is a personal observation only and doesn't speak for the committee, BTW. (I have to put that in there).
  • Robert O'Connor_6
    Robert O'Connor_6 Member Posts: 299
    listing

    i was under the impression that if an apliances as "listed " for use with out one that was Ok?

    And while I have you on the keyboard. , those charts showing liner sizing really need to be finished. I underrstand this was a funding problem at Brookhaven, Maybe NORA can kick in the funding to get it doine. To me thats an incredibly important area. I deal with lots of old unlined chimney's.