We are bidding a job where a customer wants to reuse his
existing old steam radiators and convert these to hot water.
We would like to use mono flow tees with donfoss valves on
each coil. There are 17 radiators on the system.
Has anyone seen or installed systems like this? Any problems.
existing old steam radiators and convert these to hot water.
We would like to use mono flow tees with donfoss valves on
each coil. There are 17 radiators on the system.
Has anyone seen or installed systems like this? Any problems.
0
Comments
-
Sounds like an absolute
nightmare.
A heat load calculation is a must. Without it you could never know if the EDR output via steam can be met - or needs to be - by hot water (which is "short" on output).
The system pumping and Cv ratings, monoflow tee Cv factors coupled with the Danfoss TRV Cv ratings as well - and the size of the new return(s) will be a major calculation.
If you don't do the designs properly, you may have a tough time getting paid. This job will not be cheap. It can be done and we have done one or two. None recently. You must do the math.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Opps forgot to say we are running all new piping, only rad
are being reused.0 -
piping
If you use a monoflow system you will have to compensate for the temp drop at the end if the loop. You may want to consider a two pipe radiatiator system instead. The supply temp will be the same to all of your radiators.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
> nightmare.
>
> A heat load calculation is a must.
> Without it you could never know if the EDR output
> via steam can be met - or needs to be - by hot
> water (which is "short" on output).
>
> The system
> pumping and Cv ratings, monoflow tee Cv factors
> coupled with the Danfoss TRV Cv ratings as well -
> and the size of the new return(s) will be a major
> calculation.
>
> If you don't do the designs
> properly, you may have a tough time getting paid.
> This job will not be cheap. It can be done and
> we have done one or two. None recently. You
> must do the math.
>
> _A
> HREF="http://www.heatinghelp.com/getListed.cfm?id=
> 68&Step=30"_To Learn More About This
> Professional, Click Here to Visit Their Ad in
> "Find A Professional"_/A_
0 -
As Ken said, you must do your homework
However,the output of hot water rads can be the same as steam rads if need be because the water temp can be run at 225F supply and 205 return (as long as the boiler is rated for it and you have proper system pressure) giving you an average rad temp of 215F, typically the same as steam. On the conversions I have worked on, this is typically not an issue. The highest temp one I have had is 180F average at design and the lowest was about 135F at design. Radiation capacity has never been a problem on the systems I've worked with.
Definitely check that the last radiator capacity in the loop because of the colder supply. The TRV's should balance things out if you have hot enough water.
There are lots of these steam to divertor tee conversions around here that were done in the 1960's and they work just fine.
But again, DO YOUR HOMEWORK!
Boilerpro0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements